In the main thread, the joints were described as step joints. Perhaps the leakage through those joints are expected source of the water. 100,000 cfs is a lot of water.

It looks like the bottom slabs used step joints where one slab overlapped the other. The depth of the step was only about six inches.

More worrisome -- where the slabs are broken, the rebar appears pristine and there is much damage to the concrete -- the rebar did its job. But at the joints there is virtually no sign of any reinforcing spanning the joints.


Joint -- no rebar
upload_2017-2-17_18-34-39.png

Joint -- no rebar (but lots of apparently empty dowel holes)
upload_2017-2-17_18-36-17.png

Joint -- no rebar
upload_2017-2-17_18-39-31.png

Joint -- no rebar
upload_2017-2-17_18-40-52.png

Broken slab -- lots of like-new rebar.
upload_2017-2-17_18-38-9.png

In some places there appears to be rebar ties into the ground
upload_2017-2-17_18-43-22.png

Other than these widely spaced anchors, it appears the slabs were poured on fill. There is no evidence of concrete adhered to the rock.

No evidence of sealing, although the 100k cfs rinse cycle might have cleared any evidence of that.

I do not understand the lack of ties between the slabs. And so few anchors on a slope.
 
If the slab is thick enough at the thinnest part, the variations in thickness should be immaterial
This is a very 'common sense' observation.
However, divergence concentrates internal stress of a structure, i.e. makes it fragile. Not to mention that thickness differences of concern question compliance to the design.
 
upload_2017-2-20_13-1-51.png
Drain spacing purportedly at about 20 ft. I previously estimated slab length at 52 ft. These spacings seem approximately consistent. Possible variation in spacing between drainlines. Drain channel shape consistent with prior photos. Appears to be simple box form over drainline. There was a prior comment regarding gravel backfill.

Set side forms, add gravel bed, lay drainpipe, fill to top of form w gravel, pour slab on top?

From deep in, Drawing A-389-4:
https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-510.pdf

upload_2017-2-21_21-19-20.png

This doesn't mean this is the way it ended up, but this is what they were thinking at one point. It sure does match the photo evidence, and the text descriptions, right down to the polyethylene sheet. We know the VCP pipes got resized to six inches at the recommendation of the Oroville Dam consulting board. I'll stand corrected, there is no gravel over the top of the pipe and there is no trench. If it really was built like this the perforations may only be 1/2 to 3/4 effective. This is an odd design, and could explain these cracks:

Oroville Dam Drains in The Spillway Walls - How Do They Work?

Also, the pounding of the water above puts a direct point load on the pipe from the concrete as does the rock below. Gravel all around would distribute the load. VCP pipe is subject to cracking.

This is how it's done these days:

upload_2017-2-21_21-30-52.png

The foam is for freeze protection and probably would not be necessary in Oroville. Sand is standard as a filter around the gravel to prevent fines from being removed from the foundation. In hard rock it's probably not necessary, but as we have observed, it is questionable whether the rock here is hard.
 

Attachments

  • upload_2017-2-21_21-17-32.png
    upload_2017-2-21_21-17-32.png
    233.5 KB · Views: 502
Last edited:
i apologize for lack of picture but I am on road w only tablet.

In a prior post i referred to the concrete under the sidewall as a "footing". That is inaccurate. A footing has a horizontal surface on the bottom to support loads without those loads generating sliding forces. This especially important on slopes.

The concrete under the sidewalls (and laterally doweled into the outer slabs) appears to slope with the hillside without any flat steps on the bottom side. Instead of being a footing it might be more accurate to characterize it as a "grade beam".

It appears resistance to downhill creep was provided by the bolts along the outside and the rebar angles beneath the adjacent slabs.

In the detail in the post above, note the upper slab could press against the downhill slab (consistent w concrete being strong in compression) but the upper slab did not restrain the downhill slab from sliding (thus avoiding possible tension in the concrete).

Could a phenomenon such as thermal ratcheting gradually shift the lower slabs downhill and open gaps? The less sloped upper spillway would be less prone to sliding than the portion below the knee. Sliding of the lower section could create gaps and leaks in the knee region.
 
My prior post erroneously assumed facts not in evidence. Was the concrete poured directly on the bare rock cut or was there an intervening fill to bring up the low spots in the uneven rock cut? Fill would be bad for possible downhill shifting. Uneven bare rock could provide some "tooth" which would contribute to resistance against slippage.

DWR must have tracked spillway movement via periodic surveys.
 
It appears resistance to downhill creep was provided by the bolts along the outside and the rebar angles beneath the adjacent slabs.
In this image it is evident that the "grade beam" exhibited significant variation in width. The image also shows what appear to be bolt holes which would normally be found well set back from the outer face of the beam. In the image the bolts, or other form of reinforcement is completely missing and the bolt holes are fully exposed with only the half diameter being visible on the side face of the grade beam.

I have been puzzling over this arrangement for some time. Your comment opens up the possibility that this section of the spillway "migrated" down-slope. One possible effect of that migration was to cause the outer face of the grade beam to shear off due to tension.

The problem with this interpretation is that it is insufficient to serve as the initial cause of failure. It is more likely to be the result of secondary failure once the original trigger fault took place.

Also of interest is the fact the reinforcement rods beneath the sidewall extend straight down. I interpret this to have been a consequence of the fact that whatever they were anchored to fell away beneath them rather than making them subject to a lateral displacement.

A possible sequence of events is as follows:
1) The initiating failure occurs. Water in volume enters beneath the slab
2) The flow begins to erode the weathered gabbro visible in this area [ one caveat - we do not know what the subsurface was composed of. The adjacent hillside appears to have the characteristics of glacial till rather than any form of weathered igneous rock.]
3) As the anchors are undermined, the 52' section of sidewall and the 9' 4" margin slab slips down hill and creates increased opportunity for flow beneath the slab. This movement may have been quite minor, a few millimeters or centimeters, but the displacement is sufficient to permit the entry of high speed water in volume. The Oroville area is renowned for its use of hydraulic mining.
4) The water cuts an erosion channel to the SE working beneath the sidewall.
5) The outer depth of the grade beam shears off in tension along the line of bolt holes. This is a relatively common failure location. Whatever was connected to those vertical anchors either erodes away, or drops away, or some combination.

DRAIN-SPACING_2017-2-17_17-44-39.jpg
 
My understanding is that class "A" base rock was used to construct the sub grade filling in voids in the bed rock and the bottom grade of the 15" reinforced concrete structural spill way floor section,...no " J " anchor bars were drilled and grouted into the bed rock and tied to the floor rebar mat.

How do you know this?

If you review the photographic evidence in the thread you will find little basis for your assertions.
 
My understanding is that class "A" base rock was used to construct the sub grade filling in voids in the bed rock and the bottom grade of the 15" reinforced concrete structural spill way floor section,...no " J " anchor bars were drilled and grouted into the bed rock and tied to the floor rebar mat.

#11 anchor bars in grout were installed in holes drilled into bedrock. This has been covered in the original thread, and remains of anchors found in the debris, on 10 foot separations.
 
Photographic evidence of the obvious void beneath the intact portions of the spillway slab floor proves that the concrete was not placed on bedrock but on non native erodible material that was used between the bottom of slab and bedrock

Not proved. Erodible bedrock or shifting fill are possibilities. There will be reports later with the results of expert analysis of the cause of the failure. We're trying to study the drains here, the main thread has wider discussion.
 
From deep in, Drawing A-389-4:
https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-510.pdf

upload_2017-2-21_21-19-20.png

This doesn't mean this is the way it ended up, but this is what they were thinking at one point. It sure does match the photo evidence, and the text descriptions, right down to the polyethylene sheet. We know the VCP pipes got resized to six inches at the recommendation of the Oroville Dam consulting board. I'll stand corrected, there is no gravel over the top of the pipe and there is no trench. If it really was built like this the perforations may only be 1/2 to 3/4 effective. This is an odd design, and could explain these cracks:

Oroville Dam Drains in The Spillway Walls - How Do They Work?

Also, the pounding of the water above puts a direct point load on the pipe from the concrete as does the rock below. Gravel all around would distribute the load. VCP pipe is subject to cracking.

This is how it's done these days:

upload_2017-2-21_21-30-52.png

The foam is for freeze protection and probably would not be necessary in Oroville. Sand is standard as a filter around the gravel to prevent fines from being removed from the foundation. In hard rock it's probably not necessary, but as we have observed, it is questionable whether the rock here is hard.

I looked through those dwgs the other day and went right past that joint detail. That dowel bar is close to the bottom. If the gravel base were eroded, load transfer at the joint could spall the concrete off below the bar.
 
longitudinal joint detail.jpg

Here is the detail of the longitudinal joint. It is keyed with no dowel or bar. Detail M shows sealant installed. This is from dwg A-389-4

Here is the complete dwg.

A-389-4.jpg
https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-510.pdf


It's good to compare these details with the photos compiled by wrorke:

Oroville Dam Spillway Failure

It looks like they may have added dowels to the longitudinal expansion joints between this study and final construction, but a lot of those photos seem to match these details.
 
A zoom of a pic by dierdre on the historical pics thread:

https://www.metabunk.org/pre-failur...ay-historical-images.t8410/page-2#post-202175

Shows relatively low flow, but drains appear mostly dry or just trickling.


upload_2017-2-22_16-5-15.png

But it's useful to compare to recent pics where much more flow is evident:

https://www.metabunk.org/pre-failure-oroville-dam-spillway-historical-images.t8410/#post-200806


Previously, I did a comparison between 1986 and 2017:

https://www.metabunk.org/oroville-d...lls-how-do-they-work.t8407/page-2#post-201595

It's possible that between 1969 and 1986, flow went up.
 
I looked through those dwgs the other day and went right past that joint detail. That dowel bar is close to the bottom. If the gravel base were eroded, load transfer at the joint could spall the concrete off below the bar.

Great find. I was looking at that and trying to decipher what it represented.

What I do not yet understand:

1) The vertical dimension form top of slab to the C/L of the dowel is indicated as 1'-0"
There is no dimension given for the depth of slab from C/L of the dowel to the bottom of the slab. By eyeball this dimension appears to be no more than 2" for a full slab depth of 12" The figure of 15" for depth of the cast slab has been thrown around. This 15" depth now seems incorrect.

2) Regardless of the given dimension, the photographic evidence strongly suggests that this would have been a minimal distance and that slab pour would conform with the bedrock and act to compensate for variances in the bedrock surface.

3) Para 2 suggests that in those areas of relatively soft and friable material (I will call this type of subsurface "garbbro") the contractor would be able to rip the surface and bring it to within a relatively close tolerance of the desired depth. This depth would be planar across the spillway in the area of the gabbro. In those areas where the subsurface was composed of a much harder, more competent rock (I will call this type of rock "chert") it would not be so easy to achieve a smooth and uniform surface. The slab in this area appears to vary considerably in depth.

4) It therefore seems to be a valid conclusion that the spillway is composed of two distinct slab types: 4.1) the relatively uniform gabbro slab which is situated over areas of subsurface which are known to be subject to weathering such that the uniform and smooth slab base is bonded to less competent rock. This raises a question as to the strength of that bond; and 4.2) the areas of chert in which the rock will have been resistant to ripping, in which it would have been much more difficult to obtain a uniform and relatively smooth surface. The slab in these areas would exhibit the variable depth noted in the photographic evidence, and would likely achieve a bond with a much stronger grade of rock. In addition to this bond, the slab in these areas would be mechanically locked to the subsurface due to the slab pour conforming to the high tooth of the rock surface.

5) This perspective suggests a number of variable stress risers present in the slab. It is noted that the spillway failure occurred in an area of the slope in which the material on each side of the point of failure is the reddish material which appears to be a loose and unconsolidated aggregate, easily eroded. This perspective also lends weight to the suggestion raised by wrorke with respect to possible slip.

6) From the C/L of the VCP to the joint between slabs is given the dimension 2'-0." I do not understand the reason for this dimension. Does it suggest a relationship between slab joints and the first diagonal in the french drain?

7) There is a dimension of 6" shown from the slab joint to some variation in the slab surface downstream of the joint. There is a second unreadable dimension given for something indicated just beneath the slab surface. What might this represent?
 
4) It therefore seems to be a valid conclusion that the spillway is composed of two distinct slab types: 4.1) the relatively uniform gabbro slab which is situated over areas of subsurface which are known to be subject to weathering such that the uniform and smooth slab base is bonded to less competent rock. This raises a question as to the strength of that bond; and 4.2) the areas of chert in which the rock will have been resistant to ripping, in which it would have been much more difficult to obtain a uniform and relatively smooth surface. The slab in these areas would exhibit the variable depth noted in the photographic evidence, and would likely achieve a bond with a much stronger grade of rock. In addition to this bond, the slab in these areas would be mechanically locked to the subsurface due to the slab pour conforming to the high tooth of the rock surface.
This is a very reasonable assumption, but let's put this model into the light of above-mentioned drainage issues. We shall agree that the spillway drainage is composed of two distinct water seepage-collection conditions. One for 4.1, where gabbro lays, and another for 4.2 where the slabs are locked to rock subsurface. Thus, quantities of drained water shall significantly differ between the two slab types. IMHO.
 
Great find. I was looking at that and trying to decipher what it represented.

What I do not yet understand:

1) The vertical dimension form top of slab to the C/L of the dowel is indicated as 1'-0"
There is no dimension given for the depth of slab from C/L of the dowel to the bottom of the slab. By eyeball this dimension appears to be no more than 2" for a full slab depth of 12" The figure of 15" for depth of the cast slab has been thrown around. This 15" depth now seems incorrect.

I tend toward the 15" nominal/average thickness for the slab. I cite the 7 1/2" dimension from the slab surface to the offset of the lateral expansion joint in detail A. Also, some of the other details show a 1'-3" overall slab thickness.​

2) Regardless of the given dimension, the photographic evidence strongly suggests that this would have been a minimal distance and that slab pour would conform with the bedrock and act to compensate for variances in the bedrock surface.

3) Para 2 suggests that in those areas of relatively soft and friable material (I will call this type of subsurface "garbbro") the contractor would be able to rip the surface and bring it to within a relatively close tolerance of the desired depth. This depth would be planar across the spillway in the area of the gabbro. In those areas where the subsurface was composed of a much harder, more competent rock (I will call this type of rock "chert") it would not be so easy to achieve a smooth and uniform surface. The slab in this area appears to vary considerably in depth.

I tend to agree. But the contractor would have made a significant effort to have a 'relatively' uniform slab thickness, otherwise, he wouldn't be able to calculate concrete quantities.​

4) It therefore seems to be a valid conclusion that the spillway is composed of two distinct slab types: 4.1) the relatively uniform gabbro slab which is situated over areas of subsurface which are known to be subject to weathering such that the uniform and smooth slab base is bonded to less competent rock. This raises a question as to the strength of that bond; and 4.2) the areas of chert in which the rock will have been resistant to ripping, in which it would have been much more difficult to obtain a uniform and relatively smooth surface. The slab in these areas would exhibit the variable depth noted in the photographic evidence, and would likely achieve a bond with a much stronger grade of rock. In addition to this bond, the slab in these areas would be mechanically locked to the subsurface due to the slab pour conforming to the high tooth of the rock surface.

Also, in the areas where the chert is present, the full 5'-0" depth of the #11 (1 3/8" dia) anchor bar would be grouted into the undisturbed rock. See detail B​

5) This perspective suggests a number of variable stress risers present in the slab. It is noted that the spillway failure occurred in an area of the slope in which the material on each side of the point of failure is the reddish material which appears to be a loose and unconsolidated aggregate, easily eroded. This perspective also lends weight to the suggestion raised by wrorke with respect to possible slip.

I agree. The area of initial failure is an area that would be more easily eroded. I cannot get away from the evidence that the sidewall drain in that area wasn't functioning. All the others were flowing, so it is logical there was water in that area, and if there was, it had to be going somewhere. Possibly eroding the grabbo fill under the slab, beneath the wall footer, or just outside the wall. Or all three.​

6) From the C/L of the VCP to the joint between slabs is given the dimension 2'-0." I do not understand the reason for this dimension. Does it suggest a relationship between slab joints and the first diagonal in the french drain?

This is an interesting dimension. It suggest that the VCP ran parallel to the joint. But we need to see the drainage general arrangement dwg to be sure. Also, see how the dwg shows the VCP resting ATOP the fill and up into the slab. Was that also typical in areas that had to be filled, or was there a conventional trench?​

7) There is a dimension of 6" shown from the slab joint to some variation in the slab surface downstream of the joint. There is a second unreadable dimension given for something indicated just beneath the slab surface. What might this represent?

Best I can see after blowing up the PDF, it looks to be 1/2". It looks like the edge of the slab downstream of the expansion joint is feathered 1/2" below that of the upstream edge for a 6" distance. Perhaps to be sure not to present an upraised edge to the flowing water?​
 
In the main thread, the joints were described as step joints. Perhaps the leakage through those joints are expected source of the water. 100,000 cfs is a lot of water.

I think the spillway was running at 55,000 CFS when the hole developed, but yes, it's still a lot of water. From all the photo evidence, it's apparent to me flow in the drains goes up with more flow in the spillway. There is some evidence that flow in the drains has gone up over time, imo. Stagnation pressure is the flipside of cavitation:

Various excerpts from:
https://www.usbr.gov/ssle/damsafety/risk/BestPractices/Chapters/VI-1-20150610.pdf
https://www.usbr.gov/assetmanagement/WaterBulletins/218dec06.pdf
https://www.usbr.gov/tsc/techreferences/designstandards-datacollectionguides/finalds-pdfs/DS14-3.pdf

Waterstops
For earlier designs, metal waterstops were used by Reclamation in concrete dams and in spillway crests to prevent leakage of reservoir water through contraction joints. Although not all spillway crest structures were thought to need waterstops, excessive leakage was often observed in gated spillway crest structures. Early designers did not always consider problems related to seepage through joints in spillway chutes or stilling basins. However, after about 1970, waterstops were regularly used in all flow surface joints to prevent uncontrolled seepage into or out of the foundation. By 1976, Reclamation identified potential for stagnation pressures to develop at joints that are offset into the spillway flow and started to implement defensive measures. The failure of Big Sandy Dam Spillway in 1983, and subsequent evaluation, helped define the stagnation pressure failure mode. Research to date has been limited, but it has helped designers understand problems related to stagnation pressures.
Content from External Source
It's really only been since 2007 or so, as far as I can tell that stagnation pressure has been quantified.

The evidence suggests Oroville had joint sealant, but no waterstops per se.

upload_2017-2-23_9-47-30.png
Water is flowing down the spillway at speed V, then hits a small bump. The stagnation pressure can be as high as V^2 / 2 g, where g is gravity, or the water velocity head for those familiar with the Bernoulli equation. Velocity head is converted to static head that acts as a hydraulic jack on the bottom of the slab (if not completely relieved by drains). If the displacement is the reverse in the above pic, pressures tend to go negative, and water can actually be sucked from under the slab - if bad enough, and there is no source of air to relieve the negative pressure, cavitation can occur. But the high flow in the drains may suggest cavitation is not the issue.

In stagnation, hydraulic jack occurs, meaning the high pressure develops under the slab, and it can exacerbate over time, if erosion is occuring:

Longitudinal cracks that are open will allow seepage flows from the spillway chute into the foundation. These seepage flows could initiate foundation erosion when the spillway is operating, but will be of a lower magnitude than what would occur at a transverse joint or crack with an offset into the flow.
Content from External Source
So it can be longitudinal (down spillway cracks or joints), but lateral or transverse crack are the worst. Erosion can create a void that creates even more jacking pressure. Spalling can cause it:

When spalling occurs, a deep localized offset will be present. If deep enough, spalling may compromise other defensive measures, such as waterstops or keys.

...

The concrete surfaces generally reach higher temperatures when the surfaces face direct sunlight. Expansion of the concrete on the surface can produce differential stresses throughout the concrete depth. There may be a “splitting” tensile force parallel to the surface. Reinforcement parallel to the surface creates a plane of weakness due to the reduced concrete area. Damage may be most significant in portions of the chute that have the greatest exposure to direct sunlight.
Content from External Source
If spalling occurs on the upspillway slab at a lateral joint, it can create stagnation pressures. Also, it doesn't take much of a crack to generate stagnation:

It is generally better to inspect the spillway chute for joints and cracks prior to assessing the risk. Locations where these features exist, particularly those that project into the flow, should be noted so that flows at that location can be studied in detail. A 1/8-inch offset may not be noticeable at a distance, but can produce significant stagnation pressures during the right flow conditions.

...

Many older spillways have a single layer of reinforcement. Even if the reinforcement were continuous across the joints, it may not be adequate to prevent offsets into the flow, or to keep the slabs acting together if uplift initiates. These lightly reinforced structures may also be deficient in terms of crack control. If waterstops are not flexible (which may be the case for metal waterstop or old plastic waterstops), differential movement at joints VI-1-12 may fail the waterstop.
Content from External Source
With regard to drains:

Foundation drainage can be designed to relieve uplift pressures caused by normal groundwater conditions. However, excessive inflows from joints and cracks in the concrete may exceed drain capacity (see Figures VI-1-7 and VI-1-8). Foundation drainage in older spillways was often constructed without adequate filtering. Any water flowing through the foundation could carry foundation materials into these unfiltered drains, possibly resulting in erosion, formation of a void, and eventual structural collapse of both the drainage system and the concrete above.
Content from External Source
Stagnation can pump a LOT of water beneath the slab:

upload_2017-2-23_10-22-9.png

Unit discharge is CFS per foot of crack. My rough estimate is the velocity was around 60 40 ft/s at time of failure, possibly a little more. (90' 178 feet wide spillway, flowing 8 feet deep at 55,000 CFS). The Bureau cautions the numbers in the chart above may be high, but my estimate of what is coming out each of those sidewall drains at ~50,000 cfs is on the order of 1-2 cfs. The chart says 10-20 13-26 feet of the right crack could produce that. What isn't relieved by drains, tends to build up as jacking pressure:

upload_2017-2-23_10-40-35.png

The media is speculating on cavitation, but given the drain flows, cracks, joint details, and various pics, stagnation should be considered as well. There certainly are clues:

https://www.metabunk.org/pre-failure-oroville-dam-spillway-historical-images.t8410/#post-200806

Rock anchors resist jacking pressure uplift, but if they aren't in something solid....

https://www.metabunk.org/oroville-d...way-walls-how-do-they-work.t8407/#post-201125

The apparent lack of reinforcement on longitudinal joints didn't help resist jacking pressures if they did develop:

https://www.metabunk.org/oroville-dam-spillway-failure.t8381/page-24#post-201197
 
Last edited:
I looked through those dwgs the other day and went right past that joint detail. That dowel bar is close to the bottom. If the gravel base were eroded, load transfer at the joint could spall the concrete off below the bar.

Usually, the load across the joint is carried by the overlapping lip, which is concrete under compression. No problem with that. To apply downward pressure on the dowel bar, the lower slab's support would have to be significantly eroded, because the leverage of the lower part of the slab would continue to try to lift the top of the slab until the fulcrum was far enough down the length of the slab.
 
This implies ten drains @ 6" for each 12" collector pipe that runs 200' to it's drain.

The cross sectional area of a 6" pipe is 3^2*3.14=28.16 sq. in.

For a 12" line it's 6^2*3.14=113.04 sq. in.

Despite a 10:1 ratio of drain lines to collector pipe, the cross sectional ratio is only about 4:1.

It was earlier noted that according to https://ia800302.us.archive.org/3/i...lirich/zh9californiastatew2003calirich_bw.pdf:



As such, I wonder if they sized the 6" lines primarily for self-cleaning ability, and didn't expect them to be using even a significant fraction of their flow capability?

I missed this when posted, but note that the pipes are likely at different grades (slopes), giving them different carrying capacity. From all the evidence, the collector pipe is at the slope of the spillway.
 
Moderator Note - deirdre
Just a reminder, this thread is specifically about "how the drains work". It is not about 'what caused the spillway to fail'.
As Mick mentioned a few days ago

I ask that people restrict their posts to significant new information. Please refrain from long posts speculating about the precise nature of things. If you don't actually have any information then you might as well wait and see. This is not a contest to see who comes up with the best guess.

So unless you post adds something other than your informed guesses then please consider carefully if it's signal or noise.

Posters who continue with lengthy speculations will be removed from the thread.
 
Some more important details from dwg A-389-4 that answer some questions.
https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-510.pdf (page 151)

sec f-f.jpg
Here, we learn that the longitudinal contraction joints are 20'-0" wide and the wall footing extends 9'-4" into the chute. From that, the overall inside width of the spill way would be 178'-8".

detail b.jpg

This detail shows the slab thickness to be 1'-3" and the reinforcing bar to be #5 (5/8" dia) and spaced at 12" each way. Also, at the anchor bar locations, there is 3'+ wire mesh mat buried in the slab. Presumably, that would resist pullout of the anchor bar.

edge ex jt.jpg
Here, we learn that the wall base slab (wall footing) varies in thickness as suspected by the photographs. It also proves that the wall footings were placed prior to the slabs because of the way the joint is offset.

sec e-e.jpg

Here, we learn the wall height to be 16'-0".

sec g-g.jpg

This view shows the collector pipe (6" shown, but suspected to be 12") to also be vitreous clay pipe (VCP). To me, this is important, as that type construction must have stable bedding. Otherwise, the joints will open up and allow leakage that could exacerbate a washout.

notes.jpg
Finally, the notes on the dwg specify 3,000 psi concrete, and specify the reinforcement to be covered by 3" of concrete unless otherwise noted.
 


Cracks are herringbone pattern, and spaced about 20 feet apart. (slab panels are 50 long in flow direction per Google Earth). I'm not saying it's underdrains, but....
 

Attachments

  • upload_2017-2-23_22-22-23.png
    upload_2017-2-23_22-22-23.png
    306.1 KB · Views: 525
Moderator Note - deirdre
Just a reminder, this thread is specifically about "how the drains work". It is not about 'what caused the spillway to fail'.
As Mick mentioned a few days ago
Hello!

I need to post about the drains UNDER the chute pavement: this thread title is about the drains in the walls... Where should I go?

Tks
 
Has anyone found a drawing of how the drains under the spillway are connected to their discharge point on the wall? We haven't seen pipes running along the outside of the wall, which implies that they're somehow embedded inside the wall and running for dozens of feet without weakening the wall. The drains also are somehow crossing the expansion joint which they're shown as being upstream of, but that might be happening under the fill which is next to the wall.
 
I am fairly certain that the drains are buried in the gravel outside the wall, so they are not visible from the outside and the pipes are protected.

Aaron Z
 
Yes, see sushi's post above #126, note blue circle. They are not embedded in the wall.
I should have elaborated perhaps. In the picture noted, "see sushi's post above #126", the blue circle highlights the elbow fitting which was used to connect the under drain system to the wall discharge point. There is a second such fitting shown in the right photo in deirdre's post just above, #147, at the upper edge of the photo, partially cut off. I would like to have been able to mark up both photos to show better what I was talking about but I do not have the needed capability. If this is not clear, perhaps I am missing the point, in which case this post and #146 should be removed. Thanks.
 
I am fairly certain that the drains are buried in the gravel outside the wall, so they are not visible from the outside and the pipes are protected.

Aaron Z
that's what i was thinking, would make the most sense. i had read early on an article that mentioned the drains were to take care of water fowing along the wall so the wall doesnt erode. but when i went back to look for it i couldnt find it again. ; (
 
I should have elaborated perhaps. In the picture noted, "see sushi's post above #126", the blue circle highlights the elbow fitting which was used to connect the under drain system to the wall discharge point. There is a second such fitting shown in the right photo in deirdre's post just above, #147, at the upper edge of the photo, partially cut off. I would like to have been able to mark up both photos to show better what I was talking about but I do not have the needed capability. If this is not clear, perhaps I am missing the point, in which case this post and #146 should be removed. Thanks.
duh. i havent had my coffee yet. thats EXACTLY what i was looking for but didnt notice it. heres the full photo. Thanks. :)
20170224-164333-wiea5.jpg
 
Has anyone found a drawing of how the drains under the spillway are connected to their discharge point on the wall? We haven't seen pipes running along the outside of the wall, which implies that they're somehow embedded inside the wall and running for dozens of feet without weakening the wall. The drains also are somehow crossing the expansion joint which they're shown as being upstream of, but that might be happening under the fill which is next to the wall.
In addition to the info provided in the first few posts just above this one, I think Mortarboarder is asking about the route that the pipe actually takes on its way to those wall outlets. I was talking with an engineer just last night, and we concluded that the most likely situation is that a series of adjacent under-floor drains connect to a common pipe located just outside the bottom of the wall, with that pipe matching the slope of the wall. Then, at intervals, that pipe connects with a vertical riser, the same structures that are seen in this photo, indicated by the yellow arrows:
One of these for every side drain?


Due to the downhill location of each riser from the series of drains that feed it, the head pressure is sufficient to bring the water to the top of the riser, and from there, the water takes the short path to the next wall outlet located downhill from there (note that every riser is just a short distance uphill from an outlet). What is less certain, is whether each riser is part of an independent system consisting only of a short series of drains located farther up the hill, or if the common pipe is continuous, connected to all under-floor drains and all risers in series. The first of these two options would require that there are overlapping sets of common pipes outside the wall, and though I once thought something like that was involved, I now lean toward the idea that there is single pipe outside the wall, with all drains and all risers connected to that pipe in series.

I believe that the pipe leading from near the top of the vertical riser to the wall outlet is what can be seen in the photo, gushing water from its open end (provided by Pozzolith in Post #30):

It might appear at first glance that the elevation of the broken end of the pipe is not correct to be feeding the wall outlet just downstream of there, but considering that the slope of the spillway is about 20 degrees (I seem to remember that someone posted in the spillway thread that the exact figure is 24 degrees), then when using the top of the wall as a reference to identify an imaginary line on the wall which is horizontal, the elevation of the gushing end of the pipe looks about right to have been connected there before being exposed and broken off (the photo's perspective won't allow a person to use a protractor to find a horizontal reference line, so I just "eyeballed" it, with the aid of the most prominent "drippage stain" running down from the top of the wall, which must be a vertical line).

Using this idea of the design, the common pipe that's connected to the bottom of the riser would be below the depth of erosion shown in that second photo, and thus out of sight in this view.

I had previously thought (and posted) that pipes outside the wall ran at only a slight downhill slope, thus "getting higher and higher relative to the wall", but such a system would have resulted in a very complex backfilling scenario. The situation utilizing risers which I'm now hypothesizing would work exactly the same, but would be simpler to build and would present no backfilling difficulties.

Maybe someone who knows how to find and look through the drawings that have been mentioned elsewhere can find a detail that might verify or otherwise clarify this idea.
 
Last edited:
Has anyone found a drawing of how the drains under the spillway are connected to their discharge point on the wall? We haven't seen pipes running along the outside of the wall, which implies that they're somehow embedded inside the wall and running for dozens of feet without weakening the wall. The drains also are somehow crossing the expansion joint which they're shown as being upstream of, but that might be happening under the fill which is next to the wall.

This is the dwg that I most want to see.

On your first point, the wall outlets are located in the top half of the wall, and would necessarily have to connect to the exterior collection drain considerably upstream from the outlet. If the collection pipe runs alongside the wall footing at its base, then there must be a wye connection in that pipe that then drains into the wall outlet at some distance downstream. I believe these cutouts in the footing base (see picture below) is where the underslab VCP drains run beneath the footing and connect to the collection pipe.



I don't think the collection drain are embedded inside and running lenghwise in the walls. The only wall penetrations, imo, are where the outlets are located. An internal pipe would be an expensive design. Also, none of the fractured wall pictures show any evidence of internal piping.

To you last point, the underslab drains wouldn't necessarily have to cross the expansion joints. If the joints are spaced at 60' or so, there is plenty of distance to lay those drains in a herringbone pattern, with a slight elevation decline to assure drainage.
 
022717 KCRA screencap.jpg

A screengrab from the KCRA live video.

On the left, drainage from the collection drain. In the center, what appears to be a piece of VCP drain. In some of the live shots, the piece in the center was clearly visible. Also, on the right, the collection drain was sometimes clearly visible.
 
A screengrab from the KCRA live video.
What struck me watching that video is how long the flow at the bottom of the spillway continued after the intake gates were fully closed, i.e. flow was being sustained entirely by what was coming out of the drains. Obviously the flow was much lower than when the gates were open but was still a decent amount of water.
 
how long the flow at the bottom of the spillway continued after the intake gates were fully closed, i
how long?. i scrolled through it twice and dont see where (timestamp) the flow from the gates actually stopped.

and re: @Pozzolith i see a drain but it isnt int he location your pic identifies
pipe.JPG pipe2.JPG
https://www.facebook.com/KCRA3/videos/vb.115763581513/10155073025346514/?type=3&theater


Moderator Note - deirdre
Please be aware that this is not a private chat between you all posting on this thread. Metabunk is a public information site, the goal is that ALL readers can gather information quickly and accurately without having to verify every post made.


Specifics are required. Timestamps, photos etc.
If long explanations are necessary try to start posts with either bullet points or a brief summary of the point of your post.

Thank you.
 
In the center, what appears to be a piece of VCP drain
At about 1:13 in the video the camera zooms in to what I think is the bit you've circled and it then breaks off and is carried away downstream (blue circle in image below). The red circle shows what looks like another smaller diameter pipe or bar sticking out - as Deirdre has just circled
 

Attachments

  • spillway_drain copy.jpg
    spillway_drain copy.jpg
    527 KB · Views: 399
how long?. i scrolled through it twice and dont see where (timestamp) the flow from the gates actually stopped.
Sorry, only the last gate is open at around 1hr06 (29:49 remaining) shown by the white plume on the right side of the immediate downstream face of the intake gates (there are closer shots of gates just before this):


By around 1hr09 (26:31 remaining) that white plume has disappeared, from which I have interpreted that gate was shut too:
 

Attachments

  • gates_1hr06 copy.jpg
    gates_1hr06 copy.jpg
    533.7 KB · Views: 409
  • gates_1hr09 copy.jpg
    gates_1hr09 copy.jpg
    573 KB · Views: 360
It was pointed out in the main thread that the drain pipe should run only slightly downhill to its end, and not along the bottom of the wall with 90 degree bend to go up to its exhaust port. That might look tidy in drawings, but sediment would clog the pipe at the bend.

Also, there should not be a continuous drain pipe down the 3,000 feet of spillway because it would easily develop huge velocities and pressures.
 