@Mick - post #661, figure12-25
Look at the seat plate below the girder. You, as a non professional, have looked at this connection for a few weeks now. NIST had years to study this connection. Do you see a "detail" problem Mick ?
No, but I see what you mean, could be rendering. I was talking about the plate that is at 90 degrees to the column face. This is where NIST are confusing column 79 with 81. Where you arrow "B" is pointing to.Do you mean in the image on the left you can see what looks like the girder overhanging the seat (A)?
I think that's just a rendering issue. If you look at the seat below that you can see the brown column is visible through the back of the seat. (B) When viewed from above it seems more correct (C), but now the top clip is partially invisible (D)
View attachment 4524
There does seem to be some inconsistency though in NCSTAR 1-9A, where Figure 3-12 (which is Figure 12-24) describes it as "unstiffened". But the reasoning is explicit - they modeled it as stiffened, because they knew vertical failure of the seat would not happen. It's not clear, but likely with the limited resolution they needed to add this plate to make the seat behavior more realistic, based on the more detailed simulations.External Quote:
Since vertical failure of the seat was not considered (Section 11.2.5), the connections at Columns 79 and 81 were both modeled as stiffened seats.
. What width do you think the plate was at 81?
First of all, do you see just how wrong they have got the connection detail?Please don't ask me questions to which you know the answer. It's a waste of time. Just say what it was.
^^^this is just so wrong on so many levels that i do not know where or if to start. Do not think i am being impolite because i am not. I can see how you would be so confused about this connection, NIST are contradicting themselves left right and centre here, so I can understand your confusion. What I cannot understand is your inability to recognise the obvious intent on their part to not be clear, and to present this information in such a confusing way.They explained why they did that.
There does seem to be some inconsistency though in NCSTAR 1-9A, where Figure 3-12 (which is Figure 12-24) describes it as "unstiffened". But the reasoning is explicit - they modeled it as stiffened, because they knew vertical failure of the seat would not happen. It's not clear, but likely with the limited resolution they needed to add this plate to make the seat behavior more realistic, based on the more detailed simulations.External Quote:
Since vertical failure of the seat was not considered (Section 11.2.5), the connections at Columns 79 and 81 were both modeled as stiffened seats.
It was 11". Which as you will remember is the seat width that they wrongly applied to plate 'pf' on column 79 and had to publish an erratum for, because they got caught out. This is where that "error" originated. I note you are now applying the description of 'stiffened' to connections in the same misleading was as they do in NCSTAR 1-9. They never modeled ANY of the connections as stiffened in the sense that they did not include stiffener plates.Please don't ask me questions to which you know the answer. It's a waste of time. Just say what it was.
^^^this is just so wrong on so many levels that i do not know where or if to start. Do not think i am being impolite because i am not. I can see how you would be so confused about this connection, NIST are contradicting themselves left right and centre here, so I can understand your confusion. What I cannot understand is your inability to recognise the obvious intent on their part to not be clear, and to present this information in such a confusing way.
Again, do you see the huge error in figure 12-25 ? Where the connection below the girder is totally wrong?"obvious intent"? I see normal human failings. Some poorly written of unclear parts of a report.
The thing is, we are talking about the global collapse model here. The connections had already been marked as failed in that model, based on the ANSYS model.
You need to stop talking about models that don't resemble reality and start discussing the actual building,Would the presence of the stiffeners on the seats in the global collapse model make any difference? Failure of the seats was not considered either way, so what does it matter?
You need to stop talking about models that don't resemble reality and start discussing the actual building, much as that does not suit you, for obvious reasons.
Models that you have no data for are not relevant really, because you cannot prove their veracity.This thread is about errors and omissions. Surely any errors and omissions in the model are relevant? Where else could they have omitted the stiffener plates from? Where else could they have entered incorrect dimensions?
ok, so how about we banish hypothetical models with no data that can be checked from this debate?
This thread is about errors and omissions. Surely any errors and omissions in the model are relevant? Where else could they have omitted the stiffener plates from? Where else could they have entered incorrect dimensions?
This thread is actually about the supposed conditions and temperatures that existed around the NE at floor 13 in WTC7, and their effects on the elements there. What NIST says happened to the elements is impossible, and has been proven to be so. Can you dispute this?I refer you to the reply I gave earlier.
This thread is actually about the supposed conditions and temperatures that existed around the NE at floor 13 in WTC7, and their effects on the elements there. What NIST says happened to the elements is impossible, and has been proven to be so. Can you dispute this?
NIST have been asked. They refuse to comment. These omissions and errors are indeed critical to their hypothesis as has been clearly demonstrated here. Both they, and those who defend their position, have no response except silence because of the critical blow that these facts land on their erroneous report. Their models only serve to further expose their ineptitude.I can't dispute, based on the information you have presented, and assuming those diagrams reflect construction reality, that it looks impossible for that girder to have simply walked straight off that seat to the west. It thought that was clear. The debate has been over whether that is "critical" to the collapse of the floor system.
I would certainly be interested to hear what NIST has to say.
No, their hypothesis was that column 79 became laterally unrestrained, and THEN buckled. It has been clearly demonstrated that the column would indeed have remained restrained due to the lack of failure proposed in NISTs analysis.Critical to one point of their probable collapse sequence yes. But their hypothesis has always been that Column 79 buckled.
No, their hypothesis was that column 79 became laterally unrestrained, and THEN buckled. It has been clearly demonstrated that the column would indeed have remained restrained due to the lack of failure proposed in NISTs analysis.
NISTs analysis proposes that thermal expansion of the floor system was to blame for these failures. It is beyond doubt that they overestimated the extent to which this expansion occurred. In that sense they have demonstrated themselves to be incompetent at best and deceptive at worst. There has indeed been critical omissions and errors made in their report re the collapse of WTC7. Thanks for the debate though, interesting.You have perhaps demonstrated it would not have become unrestrained starting with a walk-off of that particular girder in that way. You have not demonstrated there is no way it could have become unrestrained. NIST's analysis indicates that there would have been a lot of damage to connections and members.
No, their hypothesis was that column 79 became laterally unrestrained, and THEN buckled. It has been clearly demonstrated that the column would indeed have remained restrained due to the lack of failure proposed in NISTs analysis.
They they did analysis that confirmed this hypothesis (or at least supported it), and formulated a probable collapse sequence.External Quote:
8.2 LEADING COLLAPSE HYPOTHESIS FOR WTC 7
Based on observations and analyses of photographic and videographic records, critical study of the steel
framing, and simplified and detailed analyses to investigate possible failure modes that could lead to an
initiating event, the following leading collapse hypothesis was identified.
Initial Local Failure for Collapse Initiation
An initial local failure occurred at the lower floors (below Floor 14) of the building due to fire-induced
floor failures, leading to buckling of a critical column (the initiating event) which supported a large-span
floor bay with an area of about 200 m2 (2,000 ft2).
The leading hypothesis for the failure sequence that characterized the initial local failure was based on
fire-induced failure events in the tenant floors. Floor beams, girders, slabs, and connections heated more
quickly and to higher temperatures than the columns. Elevated temperatures in the floor elements led to
thermal expansion, with or without thermal weakening and sagging, which resulted in failure of floor
connections and/or buckling of floor beams. Sufficient floor component failures (connections and/or
beams) resulted in at least one unsupported column over multiple floors at the lower floors. This column
buckled and led to the initiation of global collapse.
Vertical Progression of Failure
Vertical progression of the initial local failure occurred up to the east penthouse, and as the large floor
bays became unable to redistribute the loads, this initial local failure brought down the interior structure
below the east penthouse.
Horizontal Progression of Failure
Triggered by damage due to the vertical failure below the east penthouse, the failure progressed
horizontally across the lower floors (in the region of Floors 5 and 7 that were much thicker and more
heavily reinforced than the rest of the floors), resulting in a progressive collapse of the entire structure.
External Quote:
Given the complexity of the modeled behavior, the global collapse analyses matched the observed
behavior reasonably well. The global collapse analyses confirmed the leading collapse hypothesis, which
was based on the available evidence.
External Quote:
The probable collapse sequence for WTC 7, based on the available data and evidence, and the
computer simulations
Mick says: Would the presence of the stiffeners on the seats in the global collapse model make any difference? Failure of the seats was not considered either way, so what does it matter?
This is not about the seat. This is about the girder stiffeners.
No, but I see what you mean, could be rendering. I was talking about the plate that is at 90 degrees to the column face. This is where NIST are confusing column 79 with 81. Where you arrow "B" is pointing to.
I was responding to something Gerry brought up:
Yeah, and the plate detail is wrong. They modeled 79 as 81, this is a huge mistake, and one that you apparently don't consider 'crucial'. I do.I was responding to something Gerry brought up:
Yeah, and the plate detail is wrong. They modeled 79 as 81, this is a huge mistake, and one that you apparently don't consider 'crucial'. I do.
Would the presence of the stiffeners on the seats in the global collapse model make any difference? Failure of the seats was not considered either way, so what does it matter?
You need to stop talking about models that don't resemble reality and start discussing the actual building
It's crucial because it is the basis that allowed NIST to claim the seat was 11". It's crucial because they did not look closely at the column 79 connection and modeled it as a totally different thing. Even without the seat plate being 90degrees off, as kawika has said, they did not include any stiffener plates. If they HAD included the stiffener plates they could not have made the 5.5" (later 6.25") claim look remotely credible. It is crucial in every way to their analysis.Then I asked you what difference it would make, and you told me the model was meaningless.
So why is it crucial?
Critical to one point of their probable collapse sequence yes. But their hypothesis has always been that Column 79 buckled.
79 cannot buckle unless the girder on floor 13 column 79 drops from its seat and starts a cascade.
I thought that we were only going to use stuff that we could back up with data?Nope. Nobody said that. NIST described that sequence of events in their "probable collapse sequence", but they did not say it was the only way it could happen, and their own siumlations don't even show that sequence.
and their own simulations don't even show that sequence.
What do you think the words 'probable collapse sequence' mean ? After years of study that is the most probable - and that most probable sequence starts with that girder dropping.
Mick, I thought this thread was meant to be about uncovering critical omissions and errors in NISTs analysis, not about speculating.Why not "a probable sequence".
But even if it's the most probably, and you've proven it wrong, what's the next most probable? And what after that?
Mick, I thought this thread was meant to be about uncovering critical omissions and errors in NISTs analysis, not about speculating.
You are now asking me to prove a negative. It's getting silly now.Sure it is, but the errors you may have identified are only critical if they are the only possible sequence. So you'd need to establish that.