Who are you quoting there?
I wasn't quoting anyone. I was inserting into your quote the correct sequence of events. And the correct sequence has been given by NIST in NSTAR 1-A, -- quite a few times. As here :- For ease I will number the sequence in red, from 1 to 4. You will note that frequently the correct sequence is given in the wrong order.
-----------------------------------------------------------------------------------------------------
pdf page 64 / 130
Fire-induced thermal expansion of the floor system surrounding Column 79 ( 1 ) led to the collapse of Floor 13, ( 2 ) which triggered a cascade of floor failures. ( 3 )
In this case, the floor beams on the east side of the building expanded enough that they pushed the girder spanning between Columns 79 and 44 to the west on the 13th floor. This movement was enough for the girder to walk off of its support at Column 79. The unsupported girder ( 2 ) and other local fire-induced damage caused Floor 13 to collapse, beginning a cascade of floor failures down to the 5th floor. ( 3 ) This left Column 79 with insufficient lateral support, and as a consequence, the column buckled eastward, ( 4 ) becoming the initial local failure for collapse initiation.
Pdf page 81 /130
Figure 2-2 shows the structural response of WTC 7 to the fire-induced damage on the east side. Floor 13 collapsed onto the floors below, causing a cascade of floor failures down to Floor 5. ( 3 ) The floor failures left Column 79 laterally unsupported and it buckled, ( 4 ) which was quickly followed by the buckling of Columns 80 and 81. The buckling of Column 79 ( 4 ) was the initiating event that led to the collapse of WTC 7, not the floor failures. ( 2 & 3 ) If Column 79 had not buckled, due to a larger section or bracing, for instance, the floor failures would not have been sufficient to initiate a progression of failure that would result in global collapse.
pdf page 84 / 130
The horizontal building motion started at nearly the same time as the cascading floor failures ( 3 ) started in the LS-DYNA analysis (-6.5 s), which preceded the buckling failure of Column 79. ( 4 )
pdf page 85 / 130
Table 3-1 ( confirms the sequence that cascade of floors preceded the 'initiating' event. )
pdf page 95 / 130
The buckling failure of Column 79 ( 4 ) between Floor 5 and Floor 14 was the initiating event that led to the global collapse of WTC 7. This resulted from thermal expansion ( 1 ) and failures of connections, beams, and girders ( 2 ) in the adjacent floor systems.
At Column 79, heating and expansion of the floor beams in the northeast corner caused the loss of connection between the column and the key girder. ( 2 )
Pdf page 96 / 130
As Floor 13 fell onto the floor below, a cascade of floor failures continued ( 3 ) until the damage reached the massive Floor 5 slab, leaving Column 79 without lateral support for nine floors. The long unsupported length of Column 79 led to its buckling failure. ( 4 )
pdf page 101 / 130
The thermal expansion of the WTC 7 floor beams ( 1 ) that initiated the probable collapse sequence occurred primarily at temperatures below approximately 400 °C (750 ºF).
-----------------------------------------------------------------------------------------------------
For ease of reference :-
( 1 ) = thermal expansion causing floor 13 to break from its shear studs and allow beams to thermally expand.
( 2 ) = Expanding beam enables the girder between 44 and 79 to walk-off its seat at 79.
( 3 ) = Floor 13 drops when the girder drops causing a cascade of floors and leaves 79 with no lateral support.
( 4 ) = column 79 buckles to 'initiate' global collapse.
All of the above are direct quotes from NIST's final report setting out their 'most likely hypothesis'.