Oroville Dam Spillway Failure

Status
Not open for further replies.
Has anyone here seen any evidence whatsoever in any picture they've looked at so far that there was Backfill Concrete used at any point in the construction of the main spillway?

No, and this point is one I have been a bit worried about. it's a can of worms though if we go down the road that some of the basic foundation preparations were inadequate, every little shadow of every little rock is going to be evidence of something. Its a hard road, but we may need to travel down it. I dont see any dental grouting or surface sealing or crack and gap grout injection, at all, anywhere in the bedrock cut that all the manuals and safety and design videos call for.
 
CRM, thanks for that information.

The info they post is missing what seems like an important value to me: inflow minus main spillway max outflow. If you can release 250k indefinitely (which is what they thought they could do, knowing it would flood downstream) then you can deal with a long period of 250k inflow. If you start off reasonably near full, and can only release 250k, you can't deal with 500k inflow for very long.

retired mech eng, given the extent of the damage I'd be surprised if they don't replace the entire spillway (but I've never designed one). It wouldn't be a big surprise to me if they take over part of the existing emergency spillway area to create a new spillway, so they can have a (somewhat) functional spillway during construction.

250K is only the main primary (concrete) spillway. The emergency handles much more:

Oroville Dam Spillway Failure

The combined capacity is well over 500K, I believe, and there is a lot of storage to burn up before you get to max elevation. I moved my post here:

https://www.metabunk.org/oroville-w...-inflow-calculations.t8406/page-3#post-201322

From that, peak inflow is actually 725K CFS for their current Probable Maximum Flood, but it looks to me that that would occur before you've topped out the water level (depends on where water level starts at). So peak inflow occurs before peak water level and that inflow dissipates in storage, reducing your required outflow.

There is no problem with flow capacity, except that the PMF appears to have grown since original design - it's the erosion.
 
In case anyone would like some additional background on how the outlet and spillway was designed, I found this report on the "Hydraulic Model Studies of the Flood Control Outlet and Spillway for Oroville Dam" insightful (particularly, the trial and error aspects of it). The short of it is that they built 1:48 and 1:72 scale models to test and finalize aspects of the outlet and spillway design before the actual construction was completed.

https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-510.pdf

View attachment 24969


Good find, and there seem to be several other Oroville documents:


https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-507.pdf
20170218-125224-we2fd.jpg



https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-508.pdf
20170218-125339-nbmfc.jpg


https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-509.pdf
20170218-125305-083io.jpg


https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-502.pdf
20170218-125557-s1h6t.jpg
 
Thanks for your detailed response. Given that you are not comfortable (nor am I) with the existing drainage system (full extent of the spillway?), would you replace the slab right up to the gates? I can't see how any of the under-slab drainage system can be replaced, or even inspected, without removing the slab?

An excellent question I think. Overall, I don't see any way to replace/update the drain system in the upper section without removing the interior panels of the spillway. One could reasonably retain the 2 sidewalls and excavate outside of them to replace the longitudinal drain piping, but the laterals or diagonals would require removal of the existing floor slabs.

To your point, I don't know that it would be necessary to go all the way to the gate house - the photo evidence we've seen seems to indicate that the drains do not become flowing until some distance down the spillway. However, it may be determined that floor panel modifications need to be made closer to the gate house in order to satisfy other design criteria.
 
An excellent question I think. Overall, I don't see any way to replace/update the drain system in the upper section without removing the interior panels of the spillway. One could reasonably retain the 2 sidewalls and excavate outside of them to replace the longitudinal drain piping, but the laterals or diagonals would require removal of the existing floor slabs.

To your point, I don't know that it would be necessary to go all the way to the gate house - the photo evidence we've seen seems to indicate that the drains do not become flowing until some distance down the spillway. However, it may be determined that floor panel modifications need to be made closer to the gate house in order to satisfy other design criteria.
I don't see any drains near the top that aren't flowing. They don't start until some distance down the hill because they need to collect water from under the slab and then flow downhill to an outlet.

Or am I missing some drains near the top that aren't flowing?
 
Thanks Mick
How good is that "rock"? From the erosion following the emergency spillway overflow, it seemed very broken with numerous cracks and faults. What confidence can we have that that "rock" is reliable? Have there been any deep core samples taken?

Simply look at the natural channels cut by the emergency spillway outflow. No significant channel erosion despite the concentrated flow. And clear blue-green bedrock shown for the length of the channel from the bottom of the bench below the weir to the river.

Add that we know the builder went to significant extra expense and effort to insure the weir is built on solid bedrock.
 
I don't see any drains near the top that aren't flowing. They don't start until some distance down the hill because they need to collect water from under the slab and then flow downhill to an outlet.

Or am I missing some drains near the top that aren't flowing?
Hi Junkie - the drainpipes collecting the under-slab water at the head of the flume can only discharge at a level lower than the collection-height.

If the flume has a slope of 5 degrees and the sides have a height of 20', the outlet of the drain pipes under the slab at the discharge gates will surface almost 300' "down-spillway". That's why there is no discharge to see in the first part of the flume.

cheers edi
 
Last edited:
How hard is it to replace the entire spillway with modern methods? I feel there is a disconnect in our society about the massive positive economic impact of the dam and the costs involved. It feels like a friend telling me they will get around to having an oil change some day when we are driving to work and their car is making awful noises. The transportation costs are part of the income plan!!!! Want peaches cheap? Better fix the dam. best memory department is driving through the orchards below this dam in spring and smelling several thousand acres of one crop ripening, in the case of the peach tree orchards it's unbelievable, like driving through a ripe peach. Gives a human a feel for what its like for animals that use their sense of smell primarily. It's sort of an amazing experience. Hope this isn't a rant but more a relation of what the dam's impact is including a personal account of the wonders of the growth cycle allowed by the irrigation the dam provides. If it's a rant delete away I understand.
 
I don't see any drains near the top that aren't flowing. They don't start until some distance down the hill because they need to collect water from under the slab and then flow downhill to an outlet.

Or am I missing some drains near the top that aren't flowing?

I believe you are correct - based on this photo from post 995 it appears that there are just 3 sets of drains between the gate house and the point the flood control channel becomes convex.

1192-jpg.24903
 
How hard is it to replace the entire spillway with modern methods?

It's time and money. Several years and over a billion dollars. Using the Folsom auxiliary spillway as an example. That cost was justified by the danger to the city of Sacramento.
 
In case anyone would like some additional background on how the outlet and spillway was designed, I found this report on the "Hydraulic Model Studies of the Flood Control Outlet and Spillway for Oroville Dam" insightful (particularly, the trial and error aspects of it). The short of it is that they built 1:48 and 1:72 scale models to test and finalize aspects of the outlet and spillway design before the actual construction was completed.

https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-510.pdf

I encourage folks to review this study regarding the flood control and spillway designs - its interesting to note how much the final constructed unit differs from the initial proposed designs, including some designs that initially included a larger outlet works for both normal and flood flow rates.
 
Question for the civil engineers - can this type of failure be modeled with open channel flow simulation software (if there is such software out there)? The objective would be to calculate dynamic and static forces on the concrete weir, all for a given range of V notch sizes/flows? Is there any way that the end of the weir could could be pushed aside, if one end were to be bypassed and a V notch formed? Or is the weir too massive to be pushed aside or pushed forward by any foreseeable flow?


There are already numerous modelling programs that can calculate different effects. I am certain simulations have been run on numerous failure modes and they know the effects of each.

The emergency weir is engineered to withstand the full force of the lake. Builders went to considerable effort and expense to insure solid bedrock as a foundation. The ogee weir is as much as 64' wide at its base and weighs somewhere in the range of 80,000 to 130,000 tons (guesstimate). The design took into account things like this and overturning etc.

The base of the weir is also significantly below grade on the reservoir side - with as little as 6 to 10' exposed at thge parking lot end.

Knowing what we do know it is highly unlikely the weir is moving anywhere. It is also unlikely backcutting from the bench below it could ever cut thru the weir or its bedrock foundation. The engineering required was well understood even back then.

It is far more likely a failure could occur at the parking lot end of the spillway. There the "wall" is small, and only several feet below grade. If backcutting reached the wall there it could easily cut under it by all appearances. That said it is more than 500 feet to deeper water (and with bedrock near the surface) and any v notch that would form would not likely have sufficient flow it would seem to grow very far ...
 
I am sure their will be (already is) lots of clamoring and finger pointing from/to all sides. The reality is almost all major rivers in CA have at least one if not multiple dams on them already. There really are not a lot of viable possibilities left that could make a significant impact in water storage.
Seems that Shasta folks are none too happy about losing any dams. Wonder if the Oroville events will strengthen objections to dam removals. Also, note quote from 45's Interior guy, to the effect that "we throw them up, not take them down."
http://www.dailytidings.com/news/20170129/yreka-meeting-attendees-say-no-to-dam-removal

External Quote:

YREKA, Calif — More than 100 people attended the last in a series of three meetings Thursday in Yreka seeking public comment on the planned removal of four dams along the Klamath River, and the overwhelming feeling expressed by Siskiyou County residents was outrage.

Many stated that the majority of the county had spoken in favor of leaving the dams in place and believe that the government entities involved in the decision were not listening to them.

Some threatened lawsuits if the dam-removal process moves forward without considering residents' concerns.
...
All essentially spoke in favor of leaving the dams in place, with Ryan stating that LaMalfa had sent her with a message for Siskiyou County citizens: "Zinke told me, 'We don't pull down dams, we put 'em up,'" in reference to President Trump's Interior Secretary pick, Rep. Ryan Zinke, R-Montana. The remark was met with cheers from the crowd.
 
Last edited by a moderator:
Well the weir is quite capable, as we have seen, of holding back the entire top of the lake. I don't think water rushing past one end is going to add that much additional force. Plus it's notched into the bedrock. Expansion of the notch would seem to be more of an issue. All very unquantified though.
Based on the earlier posted cross section of the ogee weir(post #745), there is a 4' 0" facing of enriched concrete. Given that, it's shape and it's mass , it's recent short testing ,the concrete likely can handle large smooth flows well. The major unknown is what effect a river running down that hillside will have. The first minimum effect will be substantial debris deposition in the channel. Likely , there will be some surprises in channel formation due to non - homogeneous hillside conditions . With what we've seen so far , a broad categorization of the hillside materials might be soil, frangible bedrock, and coherent bedrock . A diamond is extremely hard, yet cleaves nicely along cleavage planes. Weakpoints matter.
The major unknown and unknowable is the weather within the drainage basin, and if one cares to consider the effect on saturated full drainages down stream, that could also be taken into account. The Lake Oroville watershed is what determines flows Oroville dam and its peripheries (arguably an artificial distinction, as they are necessary components of a functioning dam system) must contain. Current Lake Oroville elevation is 854 +, an optimistic projection was to have reached 850' by Wednesday (midnight Wednesday 872'+) I don't know what the projections for the current influx for the lake elevation are. I do hope they are closer to actual results and especially hope they are not overly optimistic. The concrete spillway is far more degraded than it was two weeks ago.
I mention these points, not to cast blame, nor be alarmist, but to focus attention and clarity of thought on where things are truly at right now and what forces are determining lake elevation. Currently all releases are through the concrete spillway, please correct if the penstock (14,000cfs max) is now operational. Current concrete spillway release is 65,000cfs. I understand there has been additional new erosion on the west bank of the spillway discharge , but have not seen imagery from today which clearly illustrates the extent of this. At minimum , there's additional debris in the river channel adding to the workload of clearing that channel.
I believe some amount of water is currently held as snow in the drainage basin ( an earlier quote described this as 31", I read that to be the water content equivalent of 31" of rain, which seems high as the moisture content of snow, even were it to exist across the entire basin should be lower than rain which is 100% moisture content as judged by rain gauges, please explain) Still some amount is upstream and has not melted. 1862 warm weather did suddenly melt snow early in the season, so there is known historic precedent for this phenomena.
This year has been strange, long, and wet (150-180% of "normal" snowpack are the published numbers I read in the Los Angeles Times when they describe ongoing Sierra snow surveys). Northern California is well saturated, dams are full, river flows are high and the current NOAA forecasts for Chico posit rains, heavy at times into Tuesday with snow elevations at 6,000-6,5000. another unusual feature of some storms this year has been rain at high elevations (9,000'+ at Mammoth, in January!) I have not seen longer range forecasts for March, but am certain days will be longer, and it's likely to be still warmer overall than February . Under "normal" conditions, and with a slow even, gradual spring melt it would be a challenge to manage the spring flows. A potential complication this year is that, warm, wet storms, can transform a slow even melt into a more episodic pulse driven event. The high water capacity of the current snowload can quickly mobilize as an addition to a warm storm's rain quantity. The drainages don't distinguish between melt and rain . Water is water, flow is flow . If such were to be the case it seems , that as large a reservoir capacity as possible might provide a buffer to pulses.
This seems especially important in light of the amount of damage we've seen in the primary regulatory system of Lake Oroville. Acknowledging the real possibility of such pulses, without debating the odds of occurrence , it seems this is a more than a low risk, with very high consequence environment we are in. Weather dependent. Current downstream flow regulation is based on the concrete spillway. If that control were to be put on hold or sidelined, it does seem to be what's left is the penstock (14,000cfs - inadequate) and the emergency spillway (no flow control)....i.e. were the reservoir to fill all (or all -14,000cfs in the best case) flow into Lake Oroville would merely exit over the emergency spillway at about the rate the inflows come in with no flow regulation and no buffer for high pulses.
 
I am sure their will be (already is) lots of clamoring and finger pointing from/to all sides. The reality is almost all major rivers in CA have at least one if not multiple dams on them already. There really are not a lot of viable possibilities left that could make a significant impact in water storage.

This Jan. 29 story from the Siskiyou Daily News shows that the new Interior at least likes more dams, not fewer.

Yreka meeting attendees say no to dam removal
By Danielle Jester
"More than 100 people attended the last in a series of three meetings Thursday in Yreka seeking public comment on the planned removal of four dams along the Klamath River, and the overwhelming feeling expressed by Siskiyou County residents was outrage....
"Public officials who spoke during the meeting included Siskiyou County Board of Supervisors members, County Assessor Mike Mallory; and Erin Ryan, a staff member for state Rep. Doug LaMalfa, R-Richvale.
"All essentially spoke in favor of leaving the dams in place, with Ryan stating that LaMalfa had sent her with a message for Siskiyou County citizens: 'Zinke told me, "'We don't pull down dams, we put 'em up,'" in reference to President Trump's Interior Secretary pick, Rep. Ryan Zinke, R-Montana. The remark was met with cheers from the crowd."
 
How hard is it to replace the entire spillway with modern methods?

Why would you replace the entire Main Spillway? The top part didn't fail and appears to be holding up well under large flows. Part of the bottom failed and the erosion appears to have stopped after significant flows. By washing away the overburden on the bottom part, the bed rock is now exposed and seems to be working quite well at dispersing the energy of the flow. They probably need to modify the area where the water leaves the spillway, but I don't know that they need to put it back the way it was.

Of course we can't see what the remaining portion of the Main Spillway looks like until they turn off the water, but if it is sound, and testing shows that the drains are working and it's holding tight, I don't see that it all needs to be replaced or even rebuilt. Those decisions need to be made after the water has been turned off.
 
Are there any Sacramento River flow models in public domain? It would be interesting to see what the design plan is for keeping the Capital dry, during a warm water valley rain storm event, with primary Dam's releasing max normal flows, and Sac river weirs fully opened.

In case you haven't seen it, the NWS model output for 5 days is well formatted for civilian consumption.

Follow this link to get started.

The DWR and maybe other authorities certainly have some means by which they can manage both flood control and water delivery from and to complex networks. Pretty impressive operation.
 
That emergency spillway scenario does not seem likely, or even possible. as it would require removal of both spillways all the way to the hill past the parking lot
View attachment 24954

The parking "spillway" is only a meter or so down to rock.

So really his simulation is pretty much a "worst case spillway collapse"


Bedrock (or at least bottom of base of weir) - from my interpolation images above - is appx 836 at the main spillway end. It ramps upward from what we can tell to the parking lot which is at ~900' surface.

I think its massively unlike the main spillway end - where the weir is 64' at its base and 60 feet tall, with existing grade at appx 875 on reservoir side (meaning 39' down to base of weir) - that there would be a failure there ... and if one ever looked imminent they'd open the main spillway regardless of the damage below and largely eliminate pressure on the weir
 
Why would you replace the entire Main Spillway? The top part didn't fail and appears to be holding up well under large flows. Part of the bottom failed and the erosion appears to have stopped after significant flows. By washing away the overburden on the bottom part, the bed rock is now exposed and seems to be working quite well at dispersing the energy of the flow. They probably need to modify the area where the water leaves the spillway, but I don't know that they need to put it back the way it was.

Of course we can't see what the remaining portion of the Main Spillway looks like until they turn off the water, but if it is sound, and testing shows that the drains are working and it's holding tight, I don't see that it all needs to be replaced or even rebuilt. Those decisions need to be made after the water has been turned off.

I may be reading it wrong but I feel like you answered a statement I did not make. I asked what the difficulty would be not if it was needed. I suggested that there may be a societal issue with perception of cost of infrastructure. Your answer is directed at dismissing any need to replace a 49 year old concrete structure that has already failed significantly and was built with a lesser understanding of nearly all the issues involved than are available today. while I was not directly addressing if it needs to go, I do not agree with your statements as to why any part of it should be viewed as acceptable risk when a good portion already failed that test.

To add, it may not be physically possible to replace the main spillway, that is part of the question 'how hard would it be?'. they may need to keep the upper part as functional as possible till a point well in the future when the reservoir is very low before risking taking it out of operation to make any major changes. Don't know, just asking.

Ed:sorry 49 years not 60+ years
 
Last edited:
Good points. Can they draw it down low enough so that they can get though a rainy season without any expectation of using/needing any spillway? Perhaps someone has already crunched the numbers? And they won't be generating a lot of power with levels down that low, but I agree that is a secondary concern...

850 is the "flood control" elevation ... their normal drawdown minimum.
 
Bedrock (or at least bottom of base of weir) - from my interpolation images above - is appx 836 at the main spillway end. It ramps upward from what we can tell to the parking lot which is at ~900' surface.

I think its massively unlike the main spillway end - where the weir is 64' at its base and 60 feet tall, with existing grade at appx 875 on reservoir side (meaning 39' down to base of weir) - that there would be a failure there ... and if one ever looked imminent they'd open the main spillway regardless of the damage below and largely eliminate pressure on the weir
Thanks for your post. So if this is the case, that effectively, a "robust" invert elevation is around 900' at the emergency spillway, why don't they just use the emergency spillway again, for a least a short period where they can examine the main spillway again for damage? They must have some real concerns, or they wouldn't be putting all the effort into shoring up the hillside downstream of the emergency spillway. Or is the priority now just lowering the reservoir level to give themselves more flexibility for surges in reservoir inflow? As discussed previously, the primary spillway can only be operated in its current degraded state for a limited period of time, and we don't know if that will extend to the end of this rainy season. Sorry if rambling a bit, just not sure why the authorities don't share your confidence...
 
I may be reading it wrong but I feel like you answered a statement I did not make. I asked what the difficulty would be not if it was needed. I suggested that there may be a societal issue with perception of cost of infrastructure. Your answer is directed at dismissing any need to replace a 60+ year old concrete structure that has already failed significantly and was built with a lesser understanding of nearly all the issues involved than are available today. while I was not directly addressing if it needs to go, I do not agree with your statements as to why any part of it should be viewed as acceptable risk when a good portion already failed that test.

To add, it may not be physically possible to replace the main spillway, that is part of the question 'how hard would it be?'. they may need to keep the upper part as functional as possible till a point well in the future when the reservoir is very low before risking taking it out of operation to make any major changes. Don't know, just asking.


An exhaustive inspection will be performed ... that will I'm sure include testing and inspection below the remaining spillway panels. I suspect when repairs are done the entire spillway will be necessarily replaced ... minimal addtl costs comparatively and silly to graft a Cadillac onto a 64 Chevy ...
 
Why would you replace the entire Main Spillway?

Three good reasons immediately come to mind...

1) IF a future investigation determines that the underslab drains have substantial rusting or other mechanical failure, then leaving them in place would be inviting a boatload of future structural issues, and the location of those issues (much closer to the release gates) would pose a much higher risk to the integrity of the dam and also to the public.

2) IF a future investigation determines that the spillway was built on a foundation that was not properly prepared to spec (a situation that is looking more and more likely to me with every passing day), then the proper course of action in those cases is always to tear out the garbage and do it right.

3) Even though the upper section has not collapsed, it's still a 50 year old construction that's 1/3rd of the way thru it's reasonably expected service life that is showing signs of significant cracking and requiring periods of significant repair and maintenance. As with ALL reinforced concrete infrastructure construction in the world, your options are basically to replace it now or replace it later. Since half of the spillway is already guaranteed to need major reconstruction, then this would seem to be an opportune time to take care of the entire thing.
 
850 is the "flood control" elevation ... their normal drawdown minimum.

Here's the lake level for the last two years
20170218-162901-htl4n.jpg

So if they were okay with last year they could aim to draw it down to 750, just to be on the safe side. Of course that would need the power station working, and would take at least a couple of months to get there. I suspect they would want to just keep letting out as much water as possible until may.
 
... minimal addtl costs comparatively and silly to graft a Cadillac onto a 64 Chevy ...
Add this as #4 in my post above...I believe that a huge percentage of the expense of any major construction project is the first 10 feet. When adding feet to the project from that point forward, the added cost goes down substantially. Every piece of applicable construction equipment you can imagine will already be on site to rebuild the lower half, which will be an enormous project in its own right.
 
My early opinion is the only realistic option is to make quick short term repairs to the main spillway. Get the breach filled with rock and grout it all in place, and replace the sidewalls temporarily - perhaps set in place engineered manufactured panels or similar short term. Get something that works in a pinch.

Then build a smaller auxiliary spillway with a control structure on the edge of the parking lot. Add a hardened spillway at least past the parking lot access road.

Do some geo-testing to determine bedrock in the ravine below the parking lot road. If its bedrock as expected it probably can handle releases from the auxiliary spillway as is, perhaps after removal of surface soils.

The operating specs can mandate aggressive management of levels of the reservoir to minimize necessary outflows

Once that spillway is complete the existing main spillway can be rebuilt.
 
Thanks for your post. So if this is the case, that effectively, a "robust" invert elevation is around 900' at the emergency spillway, why don't they just use the emergency spillway again, for a least a short period where they can examine the main spillway again for damage? They must have some real concerns, or they wouldn't be putting all the effort into shoring up the hillside downstream of the emergency spillway. Or is the priority now just lowering the reservoir level to give themselves more flexibility for surges in reservoir inflow? As discussed previously, the primary spillway can only be operated in its current degraded state for a limited period of time, and we don't know if that will extend to the end of this rainy season. Sorry if rambling a bit, just not sure why the authorities don't share your confidence...
Are we certain there is high quality rock under the weir's footing for its entire length?

Comparing the design blueprints and spillway test models posted earlier: the actual photos appear to show deviations.
 
Thanks for your post. So if this is the case, that effectively, a "robust" invert elevation is around 900' at the emergency spillway, why don't they just use the emergency spillway again, for a least a short period where they can examine the main spillway again for damage? They must have some real concerns, or they wouldn't be putting all the effort into shoring up the hillside downstream of the emergency spillway. Or is the priority now just lowering the reservoir level to give themselves more flexibility for surges in reservoir inflow? As discussed previously, the primary spillway can only be operated in its current degraded state for a limited period of time, and we don't know if that will extend to the end of this rainy season. Sorry if rambling a bit, just not sure why the authorities don't share your confidence...
I think the only reason they are messing with the emergency spillway at all at this point is because of the small possibility that the main spillway suffers total failure, which is NOT expected by anyone at this time that we know of (other than some zealous youtube users). Anything short of that scenario, and my impression is that they have absolutely zero intention of ever using it again under any other circumstance. HOWEVER...if they do end up needing it again (spring thaw release rates are still to be determined), then there's no chance they will caught with their pants down twice regarding the readiness of the backup. It will be as ready as they have the capability of making it.
 
Last edited:
Bedrock (or at least bottom of base of weir) - from my interpolation images above - is appx 836 at the main spillway end. It ramps upward from what we can tell to the parking lot which is at ~900' surface.

I think its massively unlike the main spillway end - where the weir is 64' at its base and 60 feet tall, with existing grade at appx 875 on reservoir side (meaning 39' down to base of weir) - that there would be a failure there ... and if one ever looked imminent they'd open the main spillway regardless of the damage below and largely eliminate pressure on the weir

There are 2 dams, one north and one south, that could be opened to release some of the upper lake level.
saddle dam locations in GE.jpg


Nether has a channel designed for it, would be disastrous for the immediate downstream communities, but the option is there to spread the flow to 2 different areas far away from the dam. One would empty into Bidwell Canyon and the other drain south into a creek system. Bidwell Canyon saddle dam foot is apparently at 875 feet in relation to the main spillway, Parish camp foot is at the 895 foot level. According to the Height from base and Crest elevation for both from the following PDF. Both crest at 922 to match the main dam.

I have no idea if it is at all possible, but the south dam Bidwell Bar Canyon Saddle Dam is to very flat terrain relative to the spillway. It may be totally wrong to do this, it would be essentially the same horrible situation of potential back cut into the reservoir, but if that was actually taking place at the spillway the south saddle dam seems like it would flood the least individual landowners before entering the yuba watersheds management system.

I wonder if they have ever considered relocating the spillway entirely to one of those more distant saddles below lake level than the one they used next to the dam?

Also, I got confused in GE as Parish camp Saddle Dam empties into Bidwell Canyon and Bidwell Bar Canyon Saddle Dam empties to the south foothill slopes, creeks leading to the yuba river. It seems a bit odd how they are named but the documents confirm the locations.

External Quote:
2.1.3 Saddle Dams Saddle Dams include Bidwell Canyon and Parish Camp and complement Oroville Dam in containing Lake Oroville. Bidwell Canyon Saddle Dam is located two miles southeast of Oroville Dam, consisting of two separate embankments. Parish Camp Saddle Dam is located on the West Branch arm of the reservoir and is 12 miles north of Oroville Dam.
External Quote:
Table A.2.1-3.
Saddle dams technical data. Bidwell Canyon Saddle Dam
Type Earth and rockfill
Height from Base of Dam 47 ft
Crest Elevation 922 ft msl
Crest Width 30 ft
Crest Length 2,270 ft
Embankment Volume 175,000 cubic yards
Side Slope 2.5:1

Parish Camp Saddle Dam
Type Earth and rockfill
Height from Base of Dam 27 ft
Crest Elevation 922 ft msl
Crest Width 30 ft
Crest Length 280 ft
Embankment Volume 11,000 cubic yards
Side Slope 2.5:1
Source: DWR Bulletin Number 200 – Volume III and Final Construction Report
PDF here
 
I encourage folks to review this study regarding the flood control and spillway designs - its interesting to note how much the final constructed unit differs from the initial proposed designs, including some designs that initially included a larger outlet works for both normal and flood flow rates.

There's a painting of the dam at the visitor center that appears to show a design with:

a) The larger, combined outlet works you mention (including concrete apron for what I guess would be proper auxiliary flood control)

b) An unlined spillway channel

c) A spillway alignment closer to east-west than the current alignment, proceeding directly down the sub-saddle valley

738669c0b6843c40d954094d3b3f8c72.jpg
 
Current update 2/18/17 16:00 PST:

Level: 854.07 (drop of 48.51 feet from peak)
Acre feet in reservoir: 2,863,316
Inflow: 38,343
Outflow: 54,987 (They have now reduced outflow to 55,000 cfs)
Reservoir Capacity: 3,573,577
Current available storage: 711,261 Acre feet


Data from Sunday 02/12/2017 16:00 PST:

Level: 902.09
Acre feet in reservoir: 3,570,722
Inflow: 41,410
Outflow: 65,117
Available storage: 2,855 ac feet

Storm total inflow from the January 15" storm event: ~588,369 ac feet (from pint where flow reached 60,000 cfs to went back down to 60,000 cfs inflows). Total storm inflow estimated at appx 670,000 ac feet.

Conclusions:

CA AWR could shut down the spillway entirely right now and have sufficient storage for the entire 15" rain event inflow (assuming 670,000 ac ft) ... elevation would be appx 899.75


http://cdec.water.ca.gov/cgi-progs/queryF?s=ORO&d=18-Feb-2017+16:15&span=150hours
 
Hmmn, thanks for posting last year's curve for comparison . Both curves rise steeply. January start points of 2016 v. 2017 reveal (2016 ) 670' initial elevation and (2017) 725' initial elevation . Peak elevation (2016) reached in May. Perhaps representative of spring melt? After many dry years, it's likely they were managing for max capacity. I expect flood control and spillway conservation may produce a different regime this year. Likely, were one to look at longer term records management trends might emerge distinguishing dry years from wet years, likely even high enough resolution to spot large storm events. Somehow , the idea of understanding the unique conditions of a given situation keeps re-emerging as an essential operating foundation,...i.e., where are we now? How to get where we'd like to be from where we are? Personally , I keep getting hammered by that idea , and my thoughts about forcing a situation into a desired theoretical framework rightfully suffer by imposing reality. I'm deeply grateful for the insight, critique , evidence based reasoning, imagery, prints, data, personal experience and understanding you folks have assembled and offered here . The civil tone of it , in today's world , is also welcome. Thank you.
 
In case anyone would like some additional background on how the outlet and spillway was designed, I found this report on the "Hydraulic Model Studies of the Flood Control Outlet and Spillway for Oroville Dam" insightful (particularly, the trial and error aspects of it). The short of it is that they built 1:48 and 1:72 scale models to test and finalize aspects of the outlet and spillway design before the actual construction was completed.

https://www.usbr.gov/tsc/techreferences/hydraulics_lab/pubs/HYD/HYD-510.pdf

Here's a choice quote from this document:

The spillway was separated into two structures, the flood control o'itlet and a 1,740-foot-long uncontrolled overfall crest. The latter, the emergency spillway, discharged into a natural channel about 500 feet to the right or northwest of the outlets, Figure 25. Since the emergency spillway would operate only during extreme flood conditions, no model studies were made of this part of the structure.
 
3) Even though the upper section has not collapsed, it's still a 50 year old construction that's 1/3rd of the way thru it's reasonably expected service life that is showing signs of significant cracking and requiring periods of significant repair and maintenance. As with ALL reinforced concrete infrastructure construction in the world, your options are basically to replace it now or replace it later. Since half of the spillway is already guaranteed to need major reconstruction, then this would seem to be an opportune time to take care of the entire thing.

Replacing the top of the spillway gives one advantage: the remaining spillway can be examined as it is removed, as well as the rock underneath. That will provide information which can be considered in estimating what happened, and the engineers will know better what they're doing as they put in the replacement.
 
It's time and money. Several years and over a billion dollars. Using the Folsom auxiliary spillway as an example. That cost was justified by the danger to the city of Sacramento.
It will take a billion dollars and several years for the main spillway or to do the Sierra Club plan and do the emergency also?

I realize construction costs are exponentially higher now than in the 1960's and they were trying desperately to save the spillway, but if this is something that cannot be accomplished in one dry season, doesn't that mean some serious problems for the future operation of the dam?
 
Thanks for your post. So if this is the case, that effectively, a "robust" invert elevation is around 900' at the emergency spillway, why don't they just use the emergency spillway again, for a least a short period where they can examine the main spillway again for damage? They must have some real concerns, or they wouldn't be putting all the effort into shoring up the hillside downstream of the emergency spillway. Or is the priority now just lowering the reservoir level to give themselves more flexibility for surges in reservoir inflow? As discussed previously, the primary spillway can only be operated in its current degraded state for a limited period of time, and we don't know if that will extend to the end of this rainy season. Sorry if rambling a bit, just not sure why the authorities don't share your confidence...


It is an "emergency" spillway ... they are protecting and hardening it so it is available and safe for use in emergencies. Use of the spillway for significant periods or flows will cause significant downslope erosion and sedimentation into the river ... they could do it but it is not desirable or wise.

The current spillway has shown no signs of catastrophic failure. It appears to have reached a relatively stable point.

Construction on the emergency spillway has shown they can do pretty significant repairs in a short period. I have no doubt that within a short time they could fill damaged areas with rock, grout the rock with cement, and either pour a surface, come up with an engineered cement panel solution, or some other method.

Erecting temporary sidewalls could similarly be relatively quickly accomplished.

That would get them thru til summer and give them time to develop more permanent plan.
 